F17

Malfunction Decision Conditions

  • When the different between indoor intake air temperature and indoor pipe temperature is above 10°C or indoor pipe temperature is below -1.0°C.
Remark:
When the indoor standby unit is freezing, the outdoor unit transfers F17 error code to the corresponding indoor unit and H39 to other indoor unit(s).

Malfunction Caused

  • Wrong wiring connection
  • Faulty sensor
  • Faulty expansion valve

Troubleshooting

When F17 indication happens
Caution For safety reason and to prevent component breakdown, always switch off the power before remove and connect the component.
Check the system wiring connection.
Is the wiring connection ok?
NO
  • Perform Auto Wiring to correct the wiring connection.
YES
Check the indoor intake air and indoor pipe temperature sensors.
Does it conform to the sensor characteristic chart?
NO
  • Replace the indoor intake air or indoor pipe temperature sensor.
YES
Check the expansion valve
Is the expansion valve ok?
YES
  • Replace the solenoid coil or expansion valve
NO
NO
  • Replace outdoor unit PCB